Проблема с S5000PAL - мигает System Status LED.
Модераторы: Trinity admin`s, Free-lance moderator`s
Проблема с S5000PAL - мигает System Status LED.
Доброго времени суток. Недавно в серверной обнаружил SR2500ALLX (базовая конфигурация: 2xПроца 5050, 5 винтов, Raid контроллер на mid-plane т.е. активный mid-plane, 2xБП, BBU и miniDIMM) ... У него мигает System Status LED. Сервер работает с 10 января 2007. Админ который обслуживал этот сервер тупо забивал на такую мелочь. Сейчас решили разобраться с этой мигалкой.
Версия FWPackage: 5.0.1 - 0031 (при загрузке выдает что это Test Version)
Вот логи из BMC:
1 05/13/2008-18:18:08 Event Log Cleared /Event Log Disabl The BMC on S5000PAL has reported an informational assertion event for Event Log Disabl. The event has the following information: the log area has been reset and/or cleared. There is no recommended action defined for this event. BMC - LUN #0 (Channel #00h)
2 05/13/2008-18:18:16 Power Unit /Power Redundancy (#0x02) The BMC on S5000PAL has reported a warning deassertion event for Power Redundancy. The event has the following information: full redundancy has been regained. No action is required. BMC - LUN #0 (Channel #00h)
3 05/13/2008-18:18:16 Power Unit /Power Redundancy (#0x02) The BMC on S5000PAL has reported an informational assertion event for Power Redundancy. The event has the following information: full redundancy has been regained. No action is required. BMC - LUN #0 (Channel #00h)
4 05/13/2008-18:18:30 System Event #0x83 The BIOS on S5000PAL has reported an informational assertion event for System Event sensor 131. The event has the following information: Timestamp Clock Sync. Event is first of the pair. There is no recommended action defined for this event. BIOS (Channel #00h)
5 05/13/2008-18:26:29 Power Unit /Power Redundancy (#0x02) The BMC on S5000PAL has reported a warning deassertion event for Power Redundancy. The event has the following information: full redundancy has been regained. No action is required. BMC - LUN #0 (Channel #00h)
6 05/13/2008-18:26:29 Power Unit /Power Redundancy (#0x02) The BMC on S5000PAL has reported an informational assertion event for Power Redundancy. The event has the following information: full redundancy has been regained. No action is required. BMC - LUN #0 (Channel #00h)
7 05/13/2008-18:26:43 System Event #0x83 The BIOS on S5000PAL has reported an informational assertion event for System Event sensor 131. The event has the following information: Timestamp Clock Sync. Event is first of the pair. There is no recommended action defined for this event. BIOS (Channel #00h)
8 05/13/2008-18:28:16 System Event #0x01 The SMI Handler on S5000PAL has reported an informational assertion event for System Event sensor 1. The event has the following information: an OEM system boot event has occurred. There is no recommended action defined for this event. SMI Handler (Channel #00h)
9 05/13/2008-18:28:23 System ACPI Power State /ACPI State The BMC on S5000PAL has reported an informational assertion event for ACPI State. The event has the following information: S0/G0. There is no recommended action defined for this event. BMC - LUN #0 (Channel #00h)
10 05/13/2008-18:30:39 Power Unit /Power Redundancy (#0x02) The BMC on S5000PAL has reported a warning deassertion event for Power Redundancy. The event has the following information: full redundancy has been regained. No action is required. BMC - LUN #0 (Channel #00h)
11 05/13/2008-18:30:39 Power Unit /Power Redundancy (#0x02) The BMC on S5000PAL has reported an informational assertion event for Power Redundancy. The event has the following information: full redundancy has been regained. No action is required. BMC - LUN #0 (Channel #00h)
12 05/13/2008-18:30:47 System Event #0x83 The BIOS on S5000PAL has reported an informational assertion event for System Event sensor 131. The event has the following information: Timestamp Clock Sync. Event is first of the pair. There is no recommended action defined for this event. BIOS (Channel #00h)
13 05/13/2008-18:32:54 Power Unit /Power Redundancy (#0x02) The BMC on S5000PAL has reported a warning deassertion event for Power Redundancy. The event has the following information: full redundancy has been regained. No action is required. BMC - LUN #0 (Channel #00h)
14 05/13/2008-18:32:54 Power Unit /Power Redundancy (#0x02) The BMC on S5000PAL has reported an informational assertion event for Power Redundancy. The event has the following information: full redundancy has been regained. No action is required. BMC - LUN #0 (Channel #00h)
15 05/13/2008-18:33:08 System Event #0x83 The BIOS on S5000PAL has reported an informational assertion event for System Event sensor 131. The event has the following information: Timestamp Clock Sync. Event is first of the pair. There is no recommended action defined for this event. BIOS (Channel #00h)
16 05/13/2008-18:34:41 System Event #0x01 The SMI Handler on S5000PAL has reported an informational assertion event for System Event sensor 1. The event has the following information: an OEM system boot event has occurred. There is no recommended action defined for this event.
Есть предположение что проблема с одним из блоков питания (Power Unit /Power Redundancy (#0x02) The BMC on S5000PAL has reported a warning deassertion event for Power Redundancy. The event has the following information: full redundancy has been regained. No action is required).
Посоветуйте как решить данную проблему...
[/b]
Версия FWPackage: 5.0.1 - 0031 (при загрузке выдает что это Test Version)
Вот логи из BMC:
1 05/13/2008-18:18:08 Event Log Cleared /Event Log Disabl The BMC on S5000PAL has reported an informational assertion event for Event Log Disabl. The event has the following information: the log area has been reset and/or cleared. There is no recommended action defined for this event. BMC - LUN #0 (Channel #00h)
2 05/13/2008-18:18:16 Power Unit /Power Redundancy (#0x02) The BMC on S5000PAL has reported a warning deassertion event for Power Redundancy. The event has the following information: full redundancy has been regained. No action is required. BMC - LUN #0 (Channel #00h)
3 05/13/2008-18:18:16 Power Unit /Power Redundancy (#0x02) The BMC on S5000PAL has reported an informational assertion event for Power Redundancy. The event has the following information: full redundancy has been regained. No action is required. BMC - LUN #0 (Channel #00h)
4 05/13/2008-18:18:30 System Event #0x83 The BIOS on S5000PAL has reported an informational assertion event for System Event sensor 131. The event has the following information: Timestamp Clock Sync. Event is first of the pair. There is no recommended action defined for this event. BIOS (Channel #00h)
5 05/13/2008-18:26:29 Power Unit /Power Redundancy (#0x02) The BMC on S5000PAL has reported a warning deassertion event for Power Redundancy. The event has the following information: full redundancy has been regained. No action is required. BMC - LUN #0 (Channel #00h)
6 05/13/2008-18:26:29 Power Unit /Power Redundancy (#0x02) The BMC on S5000PAL has reported an informational assertion event for Power Redundancy. The event has the following information: full redundancy has been regained. No action is required. BMC - LUN #0 (Channel #00h)
7 05/13/2008-18:26:43 System Event #0x83 The BIOS on S5000PAL has reported an informational assertion event for System Event sensor 131. The event has the following information: Timestamp Clock Sync. Event is first of the pair. There is no recommended action defined for this event. BIOS (Channel #00h)
8 05/13/2008-18:28:16 System Event #0x01 The SMI Handler on S5000PAL has reported an informational assertion event for System Event sensor 1. The event has the following information: an OEM system boot event has occurred. There is no recommended action defined for this event. SMI Handler (Channel #00h)
9 05/13/2008-18:28:23 System ACPI Power State /ACPI State The BMC on S5000PAL has reported an informational assertion event for ACPI State. The event has the following information: S0/G0. There is no recommended action defined for this event. BMC - LUN #0 (Channel #00h)
10 05/13/2008-18:30:39 Power Unit /Power Redundancy (#0x02) The BMC on S5000PAL has reported a warning deassertion event for Power Redundancy. The event has the following information: full redundancy has been regained. No action is required. BMC - LUN #0 (Channel #00h)
11 05/13/2008-18:30:39 Power Unit /Power Redundancy (#0x02) The BMC on S5000PAL has reported an informational assertion event for Power Redundancy. The event has the following information: full redundancy has been regained. No action is required. BMC - LUN #0 (Channel #00h)
12 05/13/2008-18:30:47 System Event #0x83 The BIOS on S5000PAL has reported an informational assertion event for System Event sensor 131. The event has the following information: Timestamp Clock Sync. Event is first of the pair. There is no recommended action defined for this event. BIOS (Channel #00h)
13 05/13/2008-18:32:54 Power Unit /Power Redundancy (#0x02) The BMC on S5000PAL has reported a warning deassertion event for Power Redundancy. The event has the following information: full redundancy has been regained. No action is required. BMC - LUN #0 (Channel #00h)
14 05/13/2008-18:32:54 Power Unit /Power Redundancy (#0x02) The BMC on S5000PAL has reported an informational assertion event for Power Redundancy. The event has the following information: full redundancy has been regained. No action is required. BMC - LUN #0 (Channel #00h)
15 05/13/2008-18:33:08 System Event #0x83 The BIOS on S5000PAL has reported an informational assertion event for System Event sensor 131. The event has the following information: Timestamp Clock Sync. Event is first of the pair. There is no recommended action defined for this event. BIOS (Channel #00h)
16 05/13/2008-18:34:41 System Event #0x01 The SMI Handler on S5000PAL has reported an informational assertion event for System Event sensor 1. The event has the following information: an OEM system boot event has occurred. There is no recommended action defined for this event.
Есть предположение что проблема с одним из блоков питания (Power Unit /Power Redundancy (#0x02) The BMC on S5000PAL has reported a warning deassertion event for Power Redundancy. The event has the following information: full redundancy has been regained. No action is required).
Посоветуйте как решить данную проблему...
[/b]
Зачем обновлять, если возможно неисправность в блоке питания (Power Unit /Power Redundancy (#0x02) The BMC on S5000PAL has reported a warning deassertion event for Power Redundancy. The event has the following information: full redundancy has been regained. No action is required) или я ошибаюсь . И еще маленький вопросик по поводу прошивок. Стоит ли сделать Back up базы перед использованием Firmware Update Package (или это не нужно т.к. пререпрошивается все кроме Raid Bios и инициализация Raid не понадобиться)???Tert писал(а):GENA
По моему, ответ напрашивается сам собой. Вначале обновите все прошивки.
Re:
Я прошивал S5000VSA поверх сконфигурированного рейда и установленной win2k8, так вот, конфигурация рейда и соответственно данные на хардах остались нетронутыми, но это не говорит что такое может прокатить на другой платформе, контроллере и т.п. Береженого бог бережет, бекап ни когда не будет лишним.GENA писал(а): И еще маленький вопросик по поводу прошивок. Стоит ли сделать Back up базы перед использованием Firmware Update Package (или это не нужно т.к. пререпрошивается все кроме Raid Bios и инициализация Raid не понадобиться)???
- DeadMazay
- Advanced member
- Сообщения: 1743
- Зарегистрирован: 20 сен 2007, 15:07
- Откуда: Новосибирск, Мск
- Контактная информация:
Re: Проблема с S5000PAL - мигает System Status LED.
перед прошивкой следовало бы прочитать файл ридми... там порусски написано что перед прошивкой отключите жесткие диски и вытащите контроллеры если они есть... ибо ответственность на падение падет на вас...
в моей практике не было правда падений ниразу
в моей практике не было правда падений ниразу
Re: Проблема с S5000PAL - мигает System Status LED.
Знаю случай, когда на s5000vsa развалился рейд при прошивке, но там догадались прошить биос до завершения ребилда (винт вылетел до прошивки).
Re:
1) Вы опубликовали кусок лога BMC за май месяц прошлого года. Есть что либо более свежее?GENA писал(а):Зачем обновлять, если возможно неисправность в блоке питания (Power Unit /Power Redundancy (#0x02) The BMC on S5000PAL has reported a warning deassertion event for Power Redundancy. The event has the following information: full redundancy has been regained. No action is required) или я ошибаюсь . И еще маленький вопросик по поводу прошивок. Стоит ли сделать Back up базы перед использованием Firmware Update Package (или это не нужно т.к. пререпрошивается все кроме Raid Bios и инициализация Raid не понадобиться)???Tert писал(а):GENA
По моему, ответ напрашивается сам собой. Вначале обновите все прошивки.
2) Проверьте состояние кабелей питания.
3) Убедитесь, что с прошивками у Вас всё в порядке. Неоднократно бывали случаи отгрузки коллегами-конкурентами серверов на основе интеловских платформ без обновления заводских прошивок. Результатом были самые разнообразные разновидности глюков...
4) Backup надо делать ВСЕГДА и на ДВА разных носителя.